10/2 wg was never a legal install for a dryer. As a rewire you need 10/3 wg and you would need to reconfigure the dryer cord & connections.
Actually if the 10/2 was an seu cable, I know it was not, and it originated at a service panel then it would have been code compliant. NM 10/2 was never compliant even from a service panel.
Maybe a dumb question, but currently I only have the 2005 Code book and I don't see SER, SEU cables listed in there. What are they? Something added to later Code books?
SE is service entrance cable- art 338
SEU is 3 wire- 2 conductors and a wrapped ground.
SER is 4 wire- 2 conductors, neutral and wrapped round
Thanks for the input...I replaced it with 10/3 wg including a new 4 wire outlet and dryer pigtail. I wanted to prove to an associate of mine that I was correct. Thanks guys....I'm going to enjoy watching him eat crow !!!!!!
Thanks! Are they considered service entrance cables? Above or below ground? Or just general conductors?
Bill USE is another type of se cable. That is used underground. SEU and SER are allowed outdoor or indoor but not underground.
Thanks, I'm still trying to fill my brain with the resi. stuff!
Those items are not limited to use in residential applications although they are more common in those applications.
I find it interesting that many feel commercial work is more complicated than residential.
I feel it is much easier to overlook a code requirement in residential work than there is in commercial work - especially with some of the code changes made in the last 10 - 15 years.
You make a new commercial installation the way you did 15 years ago but have todays inspector look at it he may not make you change much at all.
You do the same thing with a new dwelling and you will be making a lot of changes.