Dryer outlet

Status
Not open for further replies.

dec

Member
If the NM 10/2 wg feeding a dryer outlet needs to be replaced, can NM 10/2 wg be installed or does it have to be changed to NM 10/3 wg including a new 4wire outlet ?
 
Most AHJ are going to consider total replacement like that a new branch circuit and are going to require 4 wire cable.

I myself will replace it with 4 wire cable whether an inspector is going to see it or not.

It does not pay in long run to do things incorrectly, that is why you are a professional - you are supposed to know what the right way is. If you are a handiman you do what ever costs less and still makes the dryer run and have no clue why it may not be safe.
 
10/2 wg was never a legal install for a dryer. As a rewire you need 10/3 wg and you would need to reconfigure the dryer cord & connections.
 
Thanks for the input...I replaced it with 10/3 wg including a new 4 wire outlet and dryer pigtail. I wanted to prove to an associate of mine that I was correct. Thanks guys....I'm going to enjoy watching him eat crow !!!!!!
 
Actually if the 10/2 was an seu cable, I know it was not, and it originated at a service panel then it would have been code compliant. NM 10/2 was never compliant even from a service panel.
 
Actually if the 10/2 was an seu cable, I know it was not, and it originated at a service panel then it would have been code compliant. NM 10/2 was never compliant even from a service panel.

Maybe a dumb question, but currently I only have the 2005 Code book and I don't see SER, SEU cables listed in there. What are they? Something added to later Code books?:confused:
 
Maybe a dumb question, but currently I only have the 2005 Code book and I don't see SER, SEU cables listed in there. What are they? Something added to later Code books?:confused:

SE is service entrance cable- art 338
SEU is 3 wire- 2 conductors and a wrapped ground.
SER is 4 wire- 2 conductors, neutral and wrapped round
 
Thanks for the input...I replaced it with 10/3 wg including a new 4 wire outlet and dryer pigtail. I wanted to prove to an associate of mine that I was correct. Thanks guys....I'm going to enjoy watching him eat crow !!!!!!

You should have made a bet on it for lunch of your choice. As been said 10-2 nm was never legal. What was allowed for many years was to have 2 hots and a neutral (insulated) and then bond the frame to the neutral. You did the right thing for 2 reasons even if it had been an insulated neutral when changed or replaced needed to be 4 wire.
 
Thanks, I'm still trying to fill my brain with the resi. stuff!

Those items are not limited to use in residential applications although they are more common in those applications.

I find it interesting that many feel commercial work is more complicated than residential.

I feel it is much easier to overlook a code requirement in residential work than there is in commercial work - especially with some of the code changes made in the last 10 - 15 years.

You make a new commercial installation the way you did 15 years ago but have todays inspector look at it he may not make you change much at all.

You do the same thing with a new dwelling and you will be making a lot of changes.
 
Those items are not limited to use in residential applications although they are more common in those applications.

I find it interesting that many feel commercial work is more complicated than residential.

I feel it is much easier to overlook a code requirement in residential work than there is in commercial work - especially with some of the code changes made in the last 10 - 15 years.

You make a new commercial installation the way you did 15 years ago but have todays inspector look at it he may not make you change much at all.

You do the same thing with a new dwelling and you will be making a lot of changes.

Exactly, I did residential for 20 years then went commercial. Would turn residential down now. Commercial is far easier and you need not swing like a monkey to get it done in time.
 