I have recently purchased a home and noticed that the dryer receptacle is extremely close to the hose-bib - and I wanted to move the dryer receptacle further away from the water source.
In doing so, my washer has a 4-prong plug, and I had a 4 prong (X,Y,N, and EGC) receptacle. The existing wiring to the 3 prong (X,Y,N) that I needed to remove.
My train of thought:
I have removed the 3 prong plug and relocated the wiring (X,Y, N) to my preferred location and have landed the existing wires on the appropriate terminals of the new receptacles. I have then ran a #10 Equipment grounding conductor in parallel with the feeds (as it was the only new termination left).
Question: I have ran the Equipment grounding conductor (new #10 wire) to an existing ground wire that is bonded to the water pipes (which is eventually grounded when it goes outside). Is it an issue that this Equipment grounding conductor does not go back to the panel where it is fed, or is it OK as long as it's connected to ground at a location?

In doing so, my washer has a 4-prong plug, and I had a 4 prong (X,Y,N, and EGC) receptacle. The existing wiring to the 3 prong (X,Y,N) that I needed to remove.
My train of thought:
I have removed the 3 prong plug and relocated the wiring (X,Y, N) to my preferred location and have landed the existing wires on the appropriate terminals of the new receptacles. I have then ran a #10 Equipment grounding conductor in parallel with the feeds (as it was the only new termination left).
Question: I have ran the Equipment grounding conductor (new #10 wire) to an existing ground wire that is bonded to the water pipes (which is eventually grounded when it goes outside). Is it an issue that this Equipment grounding conductor does not go back to the panel where it is fed, or is it OK as long as it's connected to ground at a location?