winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
If that grounded metal (EGC) is in fact carrying current (because the dryer was on a 3-wire cord and its chassis was touching the washer chassis, which current would be increased if the cord neutral connection was compromised), can that current induce enough current on the neutral to cause a GFCI to trip?
Or putting it another way, say I have a 12/3 cable which is carrying the hot and neutral of a GFCI protected circuit, and the nuetral only of some other circuit, whose hot is routed through another cable some distance away (obviously a bad design, although for non-metallic wiring methods, allowed by the NEC). Is there a risk of the GFCI tripping due to the unbalanced current carried in the same cable as the two GFCI protected conductors?
Cheers, Wayne
Think of the 12/3 cable as a loosely coupled transformer. Current on the EGC could induce current on the neutral, but that current would still have to flow in a complete circuit that includes the hot.
Perhaps current on the EGC could cause high frequency common mode currents that are tripping the GFCI; a couple of years back there was a thread about refrigerators tripping GFCIs...