House Doc
New member
- Stuart, FL USA
I have a dryer rated 120/240 26a. That is more than the 5000 watts as per code. Homeowner says that it trips 30 amp breaker after running for at least 5 minutes. Any thoughts or solutions?
I had a service call for that same problem about a month ago. I put an ammeter on the circuit at the panel after checking all connection and it took about 30 minutes for the breaker to trip the first time and then on a couple of minutes after that. I was reading around 24 amp current draw.
I expected that the breaker would heat up but that didn't happen. I installed a new 30 amp breaker and called after they had done all of their backed-up laundry and it still hadn't tripped.
It can be the dryer or the receptacle or arcing and heating at the breaker. Or it can be just a bad breaker.
A 30 amp breaker wll normally hold a bit more than 30 amps for 5 minutes so you should see a higher current draw at some point.
I would concur with kwire, to check the breaker's terminations. Remember that these breakers have thermal/ bimetalic elements which respond to heat. And heating of the termination will warm the breaker causing it not being able to carry the current that it should be able to carry.26 amps seems a little high, but I don't really know what some of the more modern dryers are rated at. 30 amp breaker can certainly hold for some time at 30 amps and even above. Once dryer is warmed up it will cycle the heat element so it is not like it will draw 26 amps for the entire cycle, but could for first 5-10 minutes.
check breaker terminals and bus connections, poor connection in either area will likely lead to tripping. If bus connection has been overheated don't use that space it will never work well again - also replace breaker or it will likely just burn out another bus connection.