I have a job I am bidding for that is a two family dwelling and the owner wants a 3 gang meter socket to seperate the 2 units and to also have a house panel. I've calculated the total connected load of each unit to be 94 amps, and the house panel will have a minimal load of about 10 amps for general lighting and receptacles. The owner also wants to have room for electric car chargers, and mini splits to be added in the future which would be bring their service load over 200 amps.
The only service equipment that I can find larger than 200 amp is 400 amp, so I am planning on giving them two 200 amp panels for the apartments.
My main question is, would running parallel 250kcmil aluminum conductors suffice for the service conductors feeding the meter bank?
The only service equipment that I can find larger than 200 amp is 400 amp, so I am planning on giving them two 200 amp panels for the apartments.
My main question is, would running parallel 250kcmil aluminum conductors suffice for the service conductors feeding the meter bank?