mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Ok, so this was suggested on another forum which was and is a life saver for me. However, I am still a bit puzzled on how to set the relay's settings. Should I just program both the line and transformer relays as a breaker and a half/ ring application (NUMBK=2 ESS=3 LINEI=COMB) and simply switch the through the CT switches or set the relays with the logic to consider this like a main/alternate type deal letting the relay choose to ignore or sum the input currents? The first approach is the simplest, however I am unsure if it would create any unforeseen problems.
From a PDF on applying such relays to M&T:
From a PDF on applying such relays to M&T:
M&T as Dual Breaker
The relay settings allowed a certain level of CT selection control
NUMBK – the number of breakers in the scheme
o Ring, Breaker-and-a-half, M&T all use NUMBK = 2
ESS – the source selection
o Ring, Breaker-and-a-half use ESS = 3
o M&T uses ESS = Y
LINEI – Current for the protected line
o Ring, Breaker-and-a-half use LINEI = COMB
o M&T uses LINEI = IW, the breaker 1 (Normal Breaker) current
ALINEI – the alternate current source
o For Ring and Breaker-and-a-half this setting is unavailable
o For M&T ALINEI = IX, the breaker 2 (Bus Tie Breaker) current