1011.5.3 Power source. Exit signs shall be illuminated at
all times. To ensure continued illumination for a duration of
not less than 90 minutes in case of primary power loss, the
sign illumination means shall be connected to an emergency
power system provided from storage batteries, unit equipment
or an on-site generator. The installation of the emergency
power system shall be in accordance with Section
2702.
Exception: Approved exit sign illumination means that
provide continuous illumination independent of external
power sources for a duration of not less than 90 minutes,
in case of primary power loss, are not required to be connected
to an emergency electrical system.