Dual Circuit Water Heater - Disconnect Switch

If I’m understanding your wiring diagram correctly, it appears there is a 240V circuit, and a 120/240, so a 2 pole disconnect wouldn’t work.

You’ll need two disconnects grouped together and labeled.
 
If I’m understanding your wiring diagram correctly, it appears there is a 240V circuit, and a 120/240, so a 2 pole disconnect wouldn’t work.

You’ll need two disconnects grouped together and labeled.
One power source shows L1, L2 & EGC. The second power source just shows L1 & L2

2 disconnects can be used or a feeder can be ran to a small 4 circuit load center.
 
One power source shows L1, L2 & EGC. The second power source just shows L1 & L2

2 disconnects can be used or a feeder can be ran to a small 4 circuit load center.
I like the single feeder, local 4 circuit load center idea. Cost effective.
Do you know if there's a requirement for a handle tie (for the two double pole breakers) for such an application?
 
Handle tie is not required but 225.30 has requirements for multiple circuits to one appliance.
 