I'm looking at a Lochinvar water heater cutsheet, which says upper and lower elements are both 4.5 KW. Without knowing any better, I would size the feeder to this for 9 KW / 240V = 37.5 amps. I also get spotty information that both elements do not work at the same time, which would yield only 18.75 amps. Is this typical?