This is a similar question to the one on ATS feeders. As you can see the attached drawing shows 2 generators feeding a tie box (Gens are paralleled) then to an ATS
Issues
No breaker feeding the ATS - no rated protection and single disconnect
Breakers on gensets (1 or 2 might be running) are outside - ATS inside. no single-line of site disconnect, no feeder protection for the 1600A circuit (Both gens)
Looking for input - this drawing seems wrong to me both UL and NEC
Issues
No breaker feeding the ATS - no rated protection and single disconnect
Breakers on gensets (1 or 2 might be running) are outside - ATS inside. no single-line of site disconnect, no feeder protection for the 1600A circuit (Both gens)
Looking for input - this drawing seems wrong to me both UL and NEC