Read all that traffic on wire size, and got me to questionning some things.
I'm to install 2, 120 volt, 3500 watt IWHeaters.
Seems like right at 30 amps. 125 % gets me 37.5 amps. #10 THHN copper cannot be protected above 30 amps (240.4D), so #8 THHN (55 amps) protected at 40 amps. #10 EGC (from 250.122)
By using a multiwire (Phase A, B, + one neutral)circuit to a junction box before splitting of to the 2 loads, I stay at 3 (or less) current carrying conductors.
Dual breaker with tied handles.
Am I working this out right?
Are these type of multiwire circuits more popular than I've seen (industrial, never)?
Thanks