mshields
- Boston, MA
I've got a 75kVA 480 to 208Y/120V transformer. The primary is protected by a 125% of FLA rated CB. The design calls for a 250A MCB panelboard on the secondary of the transformer. This panel feeds a 100A panel.
The contractor wants to double lug the transformer, keep the 250A feeder to the panelboard and provide a 100A feeder to the 100A panel via the second set of lugs.
Since the primary is protected at 125%, no secondary protection is required and therefore I assume I don't have to worry about the sum of the OCP's adding up to 125%. But what I am worried about is utilizing a 100A feeder off the second set of lugs.
I don't see anything in Article 450 that talks about the cable on the secondary. Did I miss it? Is this some how a tap rule related issue? In short, is this permissible?
My intuition says it's ok because if you had a transformer protected by a 250% rated OCP you could have 6 OCP's on the secondary with their cable matching the size of each of the OCP's. And the OCP's would have to be relatively small since they'd have to sum to something equal to 125% of the FLA. Right?
thanks,
Mike
thanks,
Mike