I would like to tie solar into the following service panel. See photos.
I don't think I can.
There seems to be space to the right and left of the 2 service breakers, but I think it is for other service breakers....if that. (I did not have time to open up the panel and see the busing)
1. Any way to tie in the solar?
(get a PV breaker in here and still be on the load side of the meter?)
(This reminds of three-meter service panels. In that case, the breaker space provided is for a breaker for a third meter, with a single space required to be open between the three breakers. Hence the 8 spaces.)
2. Alternatively, could I install a (N) sub panel?
It would be rated 125A,
feed it from the (E) 2p100A service breaker,
put my (N) 2p40A PV breaker in the s.p., (opposite feed of course)
and snap in a 2p100A breaker to continue to feed the old (E) s.p. inside?
Will the 2p40A PV breaker be Code compliant vis a vis the main service panel (120% rule)?
(I used to think not as it is 40 added to the 100....but it isnt "distribution" and i'm not connecting there in the MSP.)
3. Is the MSP rated 100 or 200? It has 2@ 2p100 brkrs.

I don't think I can.
There seems to be space to the right and left of the 2 service breakers, but I think it is for other service breakers....if that. (I did not have time to open up the panel and see the busing)
1. Any way to tie in the solar?
(get a PV breaker in here and still be on the load side of the meter?)
(This reminds of three-meter service panels. In that case, the breaker space provided is for a breaker for a third meter, with a single space required to be open between the three breakers. Hence the 8 spaces.)
2. Alternatively, could I install a (N) sub panel?
It would be rated 125A,
feed it from the (E) 2p100A service breaker,
put my (N) 2p40A PV breaker in the s.p., (opposite feed of course)
and snap in a 2p100A breaker to continue to feed the old (E) s.p. inside?
Will the 2p40A PV breaker be Code compliant vis a vis the main service panel (120% rule)?
(I used to think not as it is 40 added to the 100....but it isnt "distribution" and i'm not connecting there in the MSP.)
3. Is the MSP rated 100 or 200? It has 2@ 2p100 brkrs.