zener

Member
I have a customer who wants a new service w/ two meters. One 200A panel for the owner panel, and one 100a panel for the tennant. Is it legal to feed the overhead meter socket w/ 4/0 seu if the load calcs. are within the correct ampacity?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: dual meter socket

Sounds fine as long as the service entrance conductors feeding the meters are sized according to your load calculation.
 