Z zener Member Jul 20, 2005 #1 I have a customer who wants a new service w/ two meters. One 200A panel for the owner panel, and one 100a panel for the tennant. Is it legal to feed the overhead meter socket w/ 4/0 seu if the load calcs. are within the correct ampacity?
I have a customer who wants a new service w/ two meters. One 200A panel for the owner panel, and one 100a panel for the tennant. Is it legal to feed the overhead meter socket w/ 4/0 seu if the load calcs. are within the correct ampacity?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Jul 20, 2005 #2 Re: dual meter socket Sounds fine as long as the service entrance conductors feeding the meters are sized according to your load calculation.
Re: dual meter socket Sounds fine as long as the service entrance conductors feeding the meters are sized according to your load calculation.