2Broke2Sleep
Senior Member
- Location
- Florida
I am working on a boat lift that has two 3/4 Hp (40 degrees C) motors for a boat lift. I'm wiring it for 220V single phase from a CB to a fused disconnect. I did my calcs and came up with no. 12 AWG wire (minimum) with 15A dual-element time delay fuses in the disconnect, max circuit breaker size 35A. Since I was provided with 10AWG thhn for the job that's what I will be pulling. Distance to motor controller is not far. FLA is 5.8A, FLC 6.9A. I wasn't positive where to round my values up or down when determining my overload, conductor size, and ground fault calcs so I rounded down to get my fuse and CB size... Anyone see any problems here?