J jes25 Senior Member Location Midwest Occupation Electrician Sep 20, 2024 #1 So USE wire can not be ran inside per article 338. But I see the cable offered by Southwire has a dual rating as RHH. So I can run it inside after all. Agree?
So USE wire can not be ran inside per article 338. But I see the cable offered by Southwire has a dual rating as RHH. So I can run it inside after all. Agree?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 20, 2024 #2 agree