Duct Bank Concrete Reinforcing

JasonWrenn

Member
Location
Louisville,KY
We are starting a new major 3 year project, apparently the EPC convinced my engineering team to allow the elimination of rebar reinforcing in the concrete for electrical duct banks to save money. We will have dozens of major duct banks. The EPC sold the idea that Fiber would work just as well. Please give thoughts or referencing on why this is a bad idea or should not be allowed. Located in Kentucky where freeze and thaw (frostline) is an issue, also will have potential truck loading over the duct banks. I am not finding much online. Thanks
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I did many duct banks in NC where the ground freezes and thaws and never had any problems with fiber reinforced concrete, in fact some with no reinforcement at all
 

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
They use fiber reinforced for driveways. Not sure if they could use it for industrial driveways or not.
How deep will the duct banks be? Below the frost line??
How deep is required before truck loading isn't an issue?
 

PD1972

Member
Location
New York (2017 NEC)
Occupation
engineer
This is more of a civil/structural design question than an electrical question. Civil/structural engineers would have more insight on when reinforcement in a concrete duct bank is actually required.

Many times "standards" or "standard details" require things that serve no purpose, but are carried through because "this is how we have always done it" or "this bad thing happened once at this very specific location because of this very specific condition". I have seen concrete encased duct banks in the northeast (freeze/thaw, aircraft loading) without reinforcement, and to my knowledge those duct banks have not failed.
 