Duct Bank Depth

Status
Not open for further replies.
Is there a NEC code requirement for minimum burial depth for directly burried ducts and concerte encased ducts. I know each company has there own specification but I am interested in knowing the code requirement. Thanks
 
Re: Duct Bank Depth

Sections 300.5 and 300.50 and their associated Tables and Notes give a fairly comprehensive matrix of various minimum cover requirements. A little less obvious are the implied affects noted in 310.60(B)(2) and its associated diagrams and Tables.

Edit: Corrected grammer and spelling

[ September 01, 2005, 01:24 PM: Message edited by: rbalex ]
 