Duct Bank - Min concrete thickness

Status
Not open for further replies.

anbm

Senior Member
Is there a minimum concrete thickness requirement between the conduit edge (the one stays nearest duct bank edge) to duct bank edge?
NEC has rule for 2" concrete encased of conduits, will this be the case? i.e. 2" minimum.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I agree with you , don resqcapt19.
For instance, for unreinforced concrete duct bank the concrete thickness will be 11/2" but for reinforced concrete 3".
 