Re: Duct Bank
There are simply too many variables and I don't plan on being the EOR. (This site doesn't pay well enough) But Section 310.60 and following doesn't apply and Appendix B isn't enforceable.
A quick look at Table B.310.7 with its reference to Figure B.310.2, Detail 2 (Second Column) would indicate a single 600kcmil conductor in a 3 conductor/phase configuration has an ampacity of 511A in the best conditions considered by the table. The ampacity would be reduced to 480A for a 4/phase configuration per B.310.(B)(5)(a).
With all other conditions held constant, simply raising the rho to 90 would make 600kcmil unacceptable compared to Table 310.16. On the other hand, Table 310.16 is based on a more conservative ambient temperature (30C) than Table B.310.7 (20C).
As I said above, too many other variables must be considered to determine the "real" ampacity of a conductor in its "condition of use." For example Table B.310.7 is based on a conductor's temperature not conductor temperature rating of 75C. The actual rho, spacing, magnetic vs. non-magnetic ducts, ambient temperature, conductor temperature rating, etc. all must be considered.
Furthermore, the ampacity of a conductor may change as it passes through different conditions of use; e.g., from duct bank to cable tray in direct sunlight to final terminations. Unless the conductor's ampacity can be determined from direct and immediate application of a table or figure,i.e,. it "fits perfectly" with the Table or Figure, I believe a conductor's maximum ampacity should be determined under engineering supervision. JMO