jimmyglen said:
We dont mount them
On a side not what kind of unit cost do you guys use on one of these?
there seems to be a fair amount of labor in wiring them with the low voltage interconnections etc etc
It seems like an easy item to underestimate
Jim
They are very easy to underestimate as I have learned from the school of hard knocks. There are a ton of variables you usually dont have an answer to until you get on the job. Here is a list of variables I can think of. I am sure there are more.
1) Who supplies the duct detectors. EC, MC or FA contractor
2) Who installs the detector.
3) Who does the control wiring to the RTU
4) How high off the ground will they be located
5) Do you need detectors on both supply and return sides.
6) Is a remote test switch required and where will it be located
7) Is the supply 120 or 24 volt
8) Does the detector need to be monitored by the FACP
9) Do the detectors need to be reset from the FACP
10) Is the detector addressable or do I need a monitor module
The prints and specs usually don't answer these questions. Sometimes you can get answers from the fire dept. or mechanical contractor. If the job requires just a couple detectors I usually put in about 3 hours each. I also exclude suppling the detector unless something specifcally tells me to supply it.