If the International Mechanical Code (2003) is in force for your installation, see below:
606.4.1 Supervision.
The duct smoke detectors shall be connected to a fire alarm system. The actuation of a duct smoke detector shall activate a visible and audible supervisory signal at a constantly attended location.
Exceptions:
1. The supervisory signal at a constantly attended location is not required where the duct smoke detector activates the building?s alarm-indicating appliances.
2. In occupancies not required to be equipped with a fire alarm system, actuation of a smoke detector shall activate a visible and an audible signal in an approved location. Duct smoke detector trouble conditions shall activate a visible or audible signal in an approved location and shall be identified as air duct detector trouble.