Ductbank ampacity calc - does length matter?

Status
Not open for further replies.

designer82

Senior Member
Location
Boston
I just did a ductbank ampacity calculation in ETAP. There's nowhere to input ductbank length so I'm guessing it doesn't matter.
Anyone know if that is true?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The length does not change the ampacity of the conductors, but the length may require the use of larger conductors to account for voltage drop.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
The calculation usually follows the IEEE 835/1994 based on Neher and McGrath publication[The Calculation of the Temperature Rise and Load Capability of Cable Systems] or IEC 60287.

The calculation includes conductor losses and heat evacuation through different materials as insulation, sheet ,conduit [ducts] , concrete and earth. The length taken in consideration is one unit length [m,feet and so on].
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
There will be heat transfer out of the duct bank radially, in a plane perpendicular to the direction of the ducts. For an infinite length duct bank, this is the only direction of heat loss. Conduction along the wires is generally ignored. Since the heat produced is the same per unit of duct length at all points, this means that the temperature of the wire will not depend on the length of the bank.

For a finite length duct bank, the vector of heat loss near the ends will have a longitudinal (parallel to ducts) component and some heat will transfer into the soil beyond the ends of the duct bank. This will allow for slightly higher ampacity, but only for lengths which are comparable to the cross section dimension of the bank. In practice this is generally neglegible. Instead of using the simple two dimensional Neher-McGrath formulation, a three dimensional differential equation needs to be solved or approximated numerically.

The SKM modelling program may be asking for the length just to determine the voltage drop rather than the ampacity. Or it may be trying to include the very short bank case.
 