H hoya99 Member Jun 8, 2006 #1 When using a common pull box(no open wire just for pulling purposes) can you have both 120 and 277 volts in a common box with out a divider?
When using a common pull box(no open wire just for pulling purposes) can you have both 120 and 277 volts in a common box with out a divider?
B bphgravity Senior Member Location Florida Jun 8, 2006 #2 Yes. See section 300.3(C) of the NEC. Just make sure you comply with Section 210.5 / 215.12 for system identification of the conductors.
Yes. See section 300.3(C) of the NEC. Just make sure you comply with Section 210.5 / 215.12 for system identification of the conductors.