Heck even POCO substations have that same problem, but they are monitored and alarmed.
However, if the alarms aren't set up correctly, you can get into big trouble:
NERC DOCUMENT
Excerpt from linked document said:
Details
The system operator received a low-voltage alarm at 109 volts DC from a 230/69kV substation and dispatched field personnel to investigate the alarm. When field personnel arrived they determined the battery charger was not producing proper voltage. Before proper action could be taken the DC voltage continued to decay and fell below the 85 volt DC operating threshold and all protective relays began to alarm and shutdown. Additionally, control circuits became non-functional and SCADA measurements and status information became erroneous. At this point it was decided the substation and surrounding BPS was at risk if a fault occurred in the unprotected relay protection system zones; so orders were given to shed load and remove the substation from service.
(Bold added by me.)
Sometimes even the most foolproof system can be tripped up by a fool.
Another example I just read about is the "blowout preventer" on that Gulf Coast oil well. It was discovered to have 260(!) failure modes and it didn't work in this case due to modifications, faulty wiring and a dead battery!
Oooppsss...