Charlie Bob
- West Tennessee
I've a lot of these services around here in the past, i've always used 350kcmil for the ungrounded service conductors nd 4/0 for the grounded one. The double meter base that the POCO give us here comes with lugs where the specified torque is shown as size wire is 350 kcmil nd less. It's been a while before my last one so i went nd discuss with inspector what size of wire he wanted nd where in the code book he looks it up ( just to make sure we are on the same page!). He thinks we oughtta use 400 kcmil for ungrounded conductor based on the table for residential services. And 350 kcmil for grounded conductor. I agree with all that as well.
But... in this particular residential set up, having two separated 200 amp disconnects being fed from this double meter base, would you still consider this a 400 amp service?
knowing that not both houses will be using everything at all times, don't you think 400 kcmil is kinda overkill? ( i had to change the lugs in it so i could fit the 400 kcmil wire.)
What size of wire you all use in your neck of the woods?
Thank you all.
Thank you all.