duplex behind permanent cabinet

Status
Not open for further replies.
There is a 1 1/2" gap between a double duplex receptacle mounted in the gyp board wall behind a permanently installed wood cabinet.

Equipment on the cabinet shelves plug into the receptacles.

A hole through the cabinet is sufficent to allow removal of the cover plate and access the box.

I see nothing that clearly prohibits such an installation.

I've seen in other threads reference to 400.8(2), which seems like a stretch.

Am I missing something?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
As long as you can access the receptacle and box then you are fine.

I agree with Ken, 400.8(2) would not apply IMHO.

Chris
 