looking for advice on following service size for duplex and let me know if I'm doing it correct or missing anything
3300 square feet
3,300 by 3va = 9900va
Small appliances load (2 per unit) = 6000va
Laundry load (one per unit ) = 3000va
Range (one per unit) = 12,000 va
Water heater (one per unit) 9000va
Dishwasher (one per unit ) = 3000va
Dryer (one per unit ) = 10,000va
Disposal (one per unit ) = 2000va
Microwave (one per unit ) =3000va
General load =51300 va
First 10,000 at 100%
Remainder at 40%
26520va general load
ac load 4 hp = 2982 by2 =5964
heat pump load I do not know
32484 by 240= 136 amps