D domnic Senior Member Occupation Electrical Contractor Mar 15, 2022 #1 Duplex with two 100 amp serves 4 feet apart, should the ground rods be bonded to each other?????????????????????????????????????????????????????????????
Duplex with two 100 amp serves 4 feet apart, should the ground rods be bonded to each other?????????????????????????????????????????????????????????????
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 15, 2022 #2 Yes, or separate by more than 6 ft. If you bond them there is a parallel path for neutral between the two services
Yes, or separate by more than 6 ft. If you bond them there is a parallel path for neutral between the two services