If you were going to design a Service to feed a Duplex House, Can you use Table 310-15 (B)(6) for Service Entrance Conductor Size. Also if each unit will have a 125A Main Service, what size service entrance conductors would be required ( One Set to feed both units Via Gutter )

Thanks
 

ayerforce

Member
Location
Hubertus, Wisconsin
Occupation
Electrical contractor
Utilizing table 310.15(B)(6), the conductors to each INDIVIDUAL 125 ampere dwelling unit panel would need to be #2 copper or 1/0 AL. The riser conductors (between the meter socket and the service point) would be sized per table 310.16 based on the calculated load of the entire building.
 

quogueelectric

Senior Member
Location
new york
wmeek said:
If you were going to design a Service to feed a Duplex House, Can you use Table 310-15 (B)(6) for Service Entrance Conductor Size. Also if each unit will have a 125A Main Service, what size service entrance conductors would be required ( One Set to feed both units Via Gutter )

Thanks
The last duplex I did I was allowed by the poco to drop a 150a for two 100 amp panels. Check with poco first
 