Even if the entire metal interior of the receptacles were not the same the only part that would need to be the same is the metal tab that ties the two binding screws together. Having said that everyone seems to agree that the metal parts of the 15 and 20 amp devices are the same.
Is this true for the actual capacity of the interior components of the receptacle?
I always thought it was 20A
feed through, which I thought I recalled seeing on some spec sheets in the past, but can't seem to find on any more recent spec sheets.
In regards to multiple 15A general purpose receptacles being on a 20A general purpose branch circuit,
I always understood it to mean that the receptacle could be wired in a series fashion with the rest of the circuit (i.e. how some guys land the line side of the circuit on one set of terminals and load side of the circuit on the other set of terminals, which I hate and want to clarify that I always, always, always, pigtail from a splice to the receptacle itself) and the terminals themselves + the metal tab that ties the two terminals together could handle 20A, say if it were part of a 20A circuit that featured multiple 15A receptacles downstream with a load totaling 20A.
It's my understanding that the NEMA configuration limits the receptacle to 15A and that no appliance cable that could feed a 20A load could match up with that NEMA configuration. Hence the difference between the 15A configuration and the 20A configuration. Therefore the only explanation of the receptacles ability to conduct 20A would be for the situation outlined above and it begs the question of whether or not the interior components could actually handle 20A.