There seems to be some rumblings as to whether to use all 4 screws on a duplex receptacle when connecting a number of them in a "feed thru" or "daisy chain" or to splice the wires leaving a pigtail and use only 2 screws. The NEC does not require splicing unless it is a "multiwire" branch circuit and then only for the neutral. The thinking seems to be that the break away tab between the adjacent screws will heat up and melt like a fuse. Surely NEMA an UL have allowed for this and I would guess UL has run heatrun tests on the receptacles and measured the temperature rise above ambient for the tab as well as the screw connections. I have been told that even 15Amp receptacles are rated for 20 Amp feed through.
I have never had to replace a receptacle because of a melted tab. My question is "How many of these melted tabs have you run across?".