duration for CBEMA curve

Status
Not open for further replies.
What's the real definition for duration for CBEMA curve? Is it the period from the starts of disturbance till it dies out? Or is it the period when the disturbance exceeds per unit voltage? Pls help. Need to complete my fyp. Thanks a lot!
 

pqtest

Member
Re: duration for CBEMA curve

Hello-

"Duration" starts at the beginning of the disturbance.

When the disturbance exceeds the PU, that (potentially) is the equipment malfunction zone regardless of duration.

May I ask what the topic of your project is? Like FIPS Pub 94, the ITIC curve is interesting, but in my opinion no longer has any real relevance in the power quality world. The only ones who seem to use it are the manufacturers of PQ analyzers- allowing you to plot recorded events against the curve.


Mark
 

rich000

Senior Member
Re: duration for CBEMA curve

Every UPS manufacturer cares about the curve, although all UPS's typically operate and transfer within a tiny portion of the curve.
 