Hello everyone this is my first post:

I was recently taking a review class at our training center, using the MIke Holts electrical exam preparation book. In there I saw an Illustration, 11-4 unit 11 commercial load calculations. What it illustrates is fusing a disconnect for an AC unit with a minimum circuit ampacity of 23 amps and a maximum fuse size of 40 amps. Ultimately it is fused at 40 amps (225%)in this illustration #12THHN wire is used, but somewhere down the line there is a panel for sure where the number 12 THHN is protected by a 20 amp Circuit breaker.

Maybe because I am not a big student of fuses and all their characteristics, but I cannot see the sense in this because the 20 amp breaker will, in my understanding will always over ride the 40 amp fuses. so why even bother fusing that high?
 

iwire

Moderator
Staff member
Location
Massachusetts
Doyle1 said:
What it illustrates is fusing a disconnect for an AC unit with a minimum circuit ampacity of 23 amps and a maximum fuse size of 40 amps. Ultimately it is fused at 40 amps (225%)in this illustration #12THHN wire is used, but somewhere down the line there is a panel for sure where the number 12 THHN is protected by a 20 amp Circuit breaker.

I can't see the illustration but likely there is no 20 amp circuit breaker.

The 12 AWG is protected by the motor overloads in the AC unit.
 

iwire

Moderator
Staff member
Location
Massachusetts
By the way, welcome to the forum. :)

Do not feel like your not getting it, this HVAC, Motor loads, welder circuits do not follow the same rules and are not what we expect. A lot of people have trouble with these NEC sections.

Ask as many questions as you want. :)
 

Doyle1

Member
Feel like I have found a home! thanks IWIRE and CAVIE

Feel like I have found a home! thanks IWIRE and CAVIE

thanks Cavie and Iwire for your quick replies I can tell I am goingt o love this place!
 