I have installed a 5hp dust collector. The customer wishes to have better performance on a profiler machine.
They expected better performance comparable to installations in other locations.
I believe the dust collector fan is not fully loading the motor. Do you agree? What options do I have?
This is a 5hp 3Phase 460v nominal. Nameplate efficiency states 87.5% and power factor 0.92. The actual voltage is 492. I get 2A on each leg. I expected 5.4A fully loaded.
My work:
(5*746)/(492*0.875*0.92*1.73)=5.44
Please check my work. Why such a difference? Is it just the fan blade mechanics do not load motor down enough? Is this engineered head room?