I thought it seemed high. The owner told me it was 7hp. I told him I wanted to see the nameplate but the compressor is in another state. Did I use the correct calc?It is unlikely that you really have a 7hp motor. Look at the motor nameplate for the actually current. The 7 hp is very likely some type of "marketing" horsepower, such as "peak horsepower" and not a real number.
Owner said he put a cord on it and plugs it into his welder receptacleDoes it have a cord and plug? What configuration?
you were right. Nameplate says HP: Spl and Amp: 15It is unlikely that you really have a 7hp motor. Look at the motor nameplate for the actually current. The 7 hp is very likely some type of "marketing" horsepower, such as "peak horsepower" and not a real number.
Yeah those numbers are normally fudged. Does it also say 240 volts? According to T430.248 a 1 HP motor at 120 volts is about 16 amps. A 3 HP at 230 volts is 17 amps.you were right. Nameplate says HP: Spl and Amp: 15
Yes 240vYeah those numbers are normally fudged. Does it also say 240 volts? According to T430.248 a 1 HP motor at 120 volts is about 16 amps. A 3 HP at 230 volts is 17 amps.