Today I was informed by the AHJ that a gas regulator falls under 515 and therefore no electrical equipment may be installed within 5' of it. This is a new one for me as I've always thought that you had to stay 3' away and that it was a building code not NEC. I didn't know any part of a dwelling would ever be considered a hazardous location. I have the house meter 3' away from the regulator with Sch 80 PVC running within this area they're claiming is hazardous. In 25 years this has never come up. He's also saying that I can't bond the gas pipe but 250.104 (B) says I have to. Any thoughts?