Is there a code requirement (electrical, mechanical, other) that states a hood fan is to be installed over a dwelling unit range?

Thank you.
 

growler

Senior Member
Location
Atlanta,GA
Is there a code requirement (electrical, mechanical, other) that states a hood fan is to be installed over a dwelling unit range?

Thank you.

There could be a local code. From what I can see ASHRAE has developed a standard that would require some sort of ventilation.

I did a quick search and found a Home Inspector looking for a reason to write it up as a concern and their standard would be good enough for that purpose.
 

rcarroll

Senior Member
'06 IRC M1901.1
Freestanding or built-in ranges shall have a vertical clearance above the cooking top of not less than 30" to unprotected combustible material. Reduced clearances are permitted in accordance with the listing & labeling of the range hoods or appliances.

Hope this helps.
 

electricmanscott

Senior Member
Location
Boston, MA
'06 IRC M1901.1
Freestanding or built-in ranges shall have a vertical clearance above the cooking top of not less than 30" to unprotected combustible material. Reduced clearances are permitted in accordance with the listing & labeling of the range hoods or appliances.

Hope this helps.

What does this have to do with whether or not ventialtion is required? :confused:
 