This is not my area of expertise, but I'm doing a favor for very good friends that recently purchased a home and are adding central AC. I'm submitting a permit application and want to include a load calc with it. Here is the calc I did off the top off my head. When I checked it today I noticed 220.83(B) which I have some questions about that will follow.
Please check this:
1200ft? @ 3VA = 3600
2 Sm. App @ 1500 = 3000
Laundry = 1500
Range = 8000
WH= 3500
Dryer= 3000
Total = 22,600
10,000@ 100% = 10,000
12,600@ 40%= 5,040
Total = 15,040
New 7.5kw heat = 7.500
Total = 22,540
22,540?240= 94A
Existing service is 100A, did I miss anything?