Dwelling Load Calcs
jsp
Red Bud, IL
When calculating the dwelling unit load in a multi-family building using Sect 220.82 (NEC 2005), is it necessary to add anthing for spare capacity? ie: if the calculated load is 90 plus amps, is a 100 amp feeder correct?
Welcome to the forum.:)
There is nothing in the NEC that requires that you add any additional loading to a service or feeder calculation for possible future loads.
It could be a good design practice to do so though.
Chris
Thanks for the reply Chris. i saw it the same way, just not as up on residential calcs. Have a project with higher kw heat and appliances than originally planned for and trying to advise owner.