I would like to know the opinions of others concerning the 2008 nec and panel change outs. Are arcfault breakers required? Be sure to read 80.9(c) in annex H and 210.12(b).
In my opinion only new circuits would require AFCI breakers.
As far as 80.9(c) that is entirely meaningless unless your area has specifically adopted Article 80. See the note above 80.1.
Wouldn't have mentioned it if we hadn't
.... I didn't know jurisdictions didn't adopt Annex H. Do they write their own ordinance for enforcement?
Cuttler hammer and if I'm not mistaken GE manufacture two pole arcfault combination type breakers.
Yes CH is making a two pole arcfault breaker. I've seen them in new home inspections. The two pole is required for multiwire branch circuits 210.4(B).
Now back to my question.
.
I'm not looking for an argument ,I'm sincerly trying to find a solution to what I believe is going to be a very expensive poblem in older homes.
I just spoke to "Bob" at Eaton's AFCI technical assistance number, and he says that the Combination Type 2-pole AFCI will not be available until "mid 2009".Cuttler hammer and if I'm not mistaken GE manufacture two pole arcfault combination type breakers.
Back to my question. Do you have any proof?
If me saying I have seen them in the jurisdition I inspect for in new house's isn't proof, I guess I'd have to say no.
last time I looked Branch/feeder wasn't spelled combination type
80.9 Application.
(A) New Installations.
This Code applies to new installations. Buildings with construction permits dated after adoption of this Code shall comply with its requirements.
(B) Existing Installations.
Existing electrical installations that do not comply with the provisions of this Code shall be permitted to be continued in use unless the authority having jurisdiction determines that the lack of conformity with this Code presents an imminent danger to occupants. Where changes are required for correction of hazards, a reasonable amount of time shall be given for compliance, depending on the degree of the hazard.
(C) Additions, Alterations, or Repairs.
Additions, alterations, or repairs to any building, structure, or premises shall conform to that required of a new building without requiring the existing building to comply with all the requirements of this Code. Additions, alterations, installations, or repairs shall not cause an existing building to become unsafe or to adversely affect the performance of the building as determined by the authority having jurisdiction. Electrical wiring added to an existing service, feeder, or branch circuit shall not result in an installation that violates the provisions of the Code in force at the time the additions are made.
Lectricman, your quote doesn't go far enough into the sentence. When only the residential service panel is altered or repaired or a new larger panel is added, and all the existing branch circuits and feeders are simply reconnected, then the only thing added, altered or repaired is the service panel. The existing branch circuits have nothing new added, altered or repaired.80.9(C) say's alterations, additions and repairs shall conform to new work