I am in the process of preparing for a state master exam and have a question regarding dwelling unit calculations. In the Mike Holt exam prep book (2011) for the dwelling unit standard calculation, there is no mention of adding in the additional 25% for the largest motor. Is this unnecessary if you take into account the following:
1) General lighting and receptacles: sq ft *3, 3000VA small appliance, 1500VA laundry
2) 75% demand factor to nameplate of 4 or more appliances (not cooking, dryers, or ac/heating)
3) Dryer- 5000W or nameplate, whichever is greater
4) Cooking equipment using 220.55
5) AC or heat, whichever is larger
When is it appropriate to add in this additional 25% for the motors? What has me confused is looking at Example D1(b) in Annex D of the code book. I understand what they do in the example, but not when it is appropriate to do this versus the other above referenced way. Thanks