Dwelling unit, circuits required

Status
Not open for further replies.

WattsOn70

Member
Location
Dallas, TX
Hi there, as per 210.11(C)(4) in NEC'17 a new garage branch circuit is required, but in Example D1(a) it only relates the gen.lighting, small appliances, laundry and bathroom ones. Is it an omission?

thanks.
 
I believe it's not addressed in the Examples as even though its a 210 required circuit, it's not required to be a separate load in Art 220 and your Example is addressing calculated loads.
 
Augie, even though it is a required circuit, if there is a garage, does it fall under the per square foot rule so not added to base? Like circuits on a porch or dedicated appliance circuits in a kitchen?
 
220.12 states that for dwelling units the garage is not counted in the "per square foot" floor area nor is is considered in 220.14(J).
 
Ok. Forgot about that. Hmm... So, would we add it to the standard calculations then or is it just a forget about it because it is so little used circuit?
If you're trying to size your main service, I'm thinking that if you're that close that it matters, just go up a size.
 