NTesla76
Senior Member
- Location
- IA -Driftless Region
- Occupation
- Electrics
2023 NEC
Single family home has an emergency service disconnect outside (meter/main).
Bonding screw is installed in emergency service disconnect
4 wire from emergency service disconnect to interior panel.
Interior panel has equipment ground bar installed. Neutrals and grounds separated.
Grounding electrode conductors to concrete encased electrode and copper water line terminate in interior panel.
I say 250.24 does not allow this.
Another inspector says 250.118(B) Exception allows this.
Any input?
Single family home has an emergency service disconnect outside (meter/main).
Bonding screw is installed in emergency service disconnect
4 wire from emergency service disconnect to interior panel.
Interior panel has equipment ground bar installed. Neutrals and grounds separated.
Grounding electrode conductors to concrete encased electrode and copper water line terminate in interior panel.
I say 250.24 does not allow this.
Another inspector says 250.118(B) Exception allows this.
Any input?