Yes, but it would also make sense to not have all the lighting in the unit fail at once if that circuit trips.Let's say the lighting load for an apartment is 1,000 VA, wouldn't it make sense to just separate the lighting load from the receptacle load and put all the lighting on one dedicated circuit?
I have seen breakers trip when an incandescent lamp burns out. I think that a short length of the filiment drops across the "bus" in the lamp and causes a short circuit. Have also seen breaker trips from a failed ballast.That is a good point.
I would think that the possibility of one 10 amp lighting circuit failing is low if only lighting is connected. Also when lighting is combined with receptacle loads on the same circuit, there is the possibility of lights flickering or dimming when vacuums or other high power loads are plugged in. Something else to consider too.
Are there any restrictions in putting an entire apartment dwelling unit?s lighting all on one circuit if the load is small enough?
Are there any restrictions in putting an entire apartment dwelling unit?s lighting all on one circuit if the load is small enough?