Dwelling unit load calculations - confused by example in exam prep book (2020)

ChesterDawg

Member
Location
CA
Hi,
I'm going through the 2020 version of the exam prep book and I'm confused by the first example question for a dwelling unit load calculation.

The calculations end up coming up with 322 amps, but the answer says to use a 400 amp disconnect.

350 amps is listed as a standard breaker size in 240.6(a) and also listed in 310.12 as a service size.

What am I missing?

thanks

]
 
I think the answer may be based on using a fusible disconnect, but those are rare now days. You are correct that a 350 amp enclosed breaker could be used for this service as long as it is listed as suitable for use as service equipment.
 
Thank you. I felt like I was missing some final step in the load calculation, but I couldn't find what it was in the code book.

Feeling better about just chalking it up to an error/outdated information in the exam prep book now.
 
Thank you. I felt like I was missing some final step in the load calculation, but I couldn't find what it was in the code book.

Feeling better about just chalking it up to an error/outdated information in the exam prep book now.
Out dated books will do this. I know all about this
 
You could write to "content" "@mikeholt.com" and report the issue with the exam prep material.
There are also a much wider array of fuses out there, compared to breakers: a fused disconnect can be more finely tailored.
 