Good Day Gentlemen,
I have recently designed a Hotel in the ?OC? (Orange County, CA) which I?ve interpreted the NEC in one manner and the inspector another. I invite your opinions ?Please?. The dwgs went through plan check and although they too miss things construction is starting and time is of the essence ?I have interpreted section 210 .11(c)(3) to be applied to Dwelling units only therefore I designed the Hotel rooms with two circuits using one circuit for the bathroom lighting, (vanity and overhead lighting) the counter GFCI as well as two entry way connivance receptacles and the other for around the room, the inspector is asking that I design the rooms with one dedicated circuit for the bathrooms GFCI, as if it was dwelling unit. Am I missing something?
I have recently designed a Hotel in the ?OC? (Orange County, CA) which I?ve interpreted the NEC in one manner and the inspector another. I invite your opinions ?Please?. The dwgs went through plan check and although they too miss things construction is starting and time is of the essence ?I have interpreted section 210 .11(c)(3) to be applied to Dwelling units only therefore I designed the Hotel rooms with two circuits using one circuit for the bathroom lighting, (vanity and overhead lighting) the counter GFCI as well as two entry way connivance receptacles and the other for around the room, the inspector is asking that I design the rooms with one dedicated circuit for the bathrooms GFCI, as if it was dwelling unit. Am I missing something?