Mitch22123
- Arizona
- Plans Examiner
Hello all,
I am a new residential plans examiner (new to the 2017 NEC, have been using the 2018 IRC) trying to learn how to calculate the load of a service panel based on a picture of the panel schedule (this is all my AHJ requires). Mainly, this has been for de-rating of the main breaker for solar additions to meet 705.12. I have been confused with how to calculate in the HVAC loads. Many of the houses here are using 2 A/C units, and I have heard a multitude of different ways I should be calculating these.
My questions are:
1. Working off of a panel schedule only, is using the MCB x .8 an approved way to calculate the load of the appliance?
2. Where do the Air handler circuits fall into this? Typically I will see 1 or 2 15A circuits for them. Are these calculated at 100%?
3. With multiple AC units, are both units calculated at 100%?
Example:
1500 SQFT Dwelling Unit, has a microwave 15A, dryer 20A, refrigerator 15A, disposal 15A, cooktop 40A, dishwasher 15A, 2 A/C units 40A & 30A condenser circuits, (x2) 15A air handler circuits.
1500 x 3VA = 4500VA
Small appliance x2 = 3000VA
Laundry = 1500VA
Microwave = 1500VA
Dryer = 5000VA
Refer= 1200VA
Disposal = 700VA
Cooktop = 7680VA
Dishwasher = 1500VA
Total = 25,180VA
Using the optional method 220.82
First 10k @ 100%= 10,000VA
15,180VA Remaining
Remainder @ 40% = 6072VA
Total = 16,072VA
AC @ 100%=
AC1 = 7680VA
AC2 = 5760VA
AH1 = 1500VA
AH2 = 1500VA
Total = 32,512VA
Total Amps = 136A
Thank you for the help in advance.
My questions are:
Example:
1500 x 3VA = 4500VA
Laundry = 1500VA
Microwave = 1500VA
Dryer = 5000VA
Refer= 1200VA
Disposal = 700VA
Cooktop = 7680VA
Dishwasher = 1500VA
Total = 25,180VA
15,180VA Remaining
Total = 16,072VA
AC @ 100%=
AC1 = 7680VA
AC2 = 5760VA
AH1 = 1500VA
AH2 = 1500VA
Total = 32,512VA
Total Amps = 136A