Dwelling unit service load- continuous or not?

Status
Not open for further replies.
You do not need to apply 125%, IMO. I would not consider any of the dwelling unit loads to be continuous.

Seems reasonable to me, but I am very surprised the NEC doesn't explicitly say whether dwelling unit calcs are subject to continuous or non-continuous load limitations. Seems like a gaping hole.
 
Seems reasonable to me, but I am very surprised the NEC doesn't explicitly say whether dwelling unit calcs are subject to continuous or non-continuous load limitations. Seems like a gaping hole.

It seems to me that the NEC doesn't explicitly say that any type of load is continuous or non-continuous. It's up to you to decide that.

(The NEC does tell you to consider several types of branch circuit loads as continuous for the purpose of branch circuit conductor sizing, but that's a different issue.)
 
I have my dwelling unit service load calculated per 220.82 as 180A. Can I use a 200A service or do I need to apply 125% = 225A?

You would never (well almost never I guess) call the entire service load continuos.

You would pick and choose which specific loads were continuos and include them at 125% in your calculations.

One item in many homes the NEC tells us to consider continuos is storage type electric water heaters.
 
It seems to me that the NEC doesn't explicitly say that any type of load is continuous or non-continuous. It's up to you to decide that.

(The NEC does tell you to consider several types of branch circuit loads as continuous for the purpose of branch circuit conductor sizing, but that's a different issue.)

Funny, I have always thought this as well, then I stumbled upon Art 422-13. :)

Never mind, didn't read your second sentence completely :eek:
 