I have my dwelling unit service load calculated per 220.82 as 180A. Can I use a 200A service or do I need to apply 125% = 225A?
I have my dwelling unit service load calculated per 220.82 as 180A. Can I use a 200A service or do I need to apply 125% = 225A?
You do not need to apply 125%, IMO. I would not consider any of the dwelling unit loads to be continuous.
Seems reasonable to me, but I am very surprised the NEC doesn't explicitly say whether dwelling unit calcs are subject to continuous or non-continuous load limitations. Seems like a gaping hole.
I have my dwelling unit service load calculated per 220.82 as 180A. Can I use a 200A service or do I need to apply 125% = 225A?
It seems to me that the NEC doesn't explicitly say that any type of load is continuous or non-continuous. It's up to you to decide that.
(The NEC does tell you to consider several types of branch circuit loads as continuous for the purpose of branch circuit conductor sizing, but that's a different issue.)